What is the minimum setting in REF relay because i am
facing some problem whenever power resumes after power
failure my transformer is tripping because of REF trip. I
am using CSPC make numerical relay(DIP switches). Now
setting is 15 percentage. What is the reason for this
triping. I sm waiting for answer
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Your setting is 15% of In.While charging ,Tr draws initial
magnetizing current 6 to 15 times the In. Any difference in
measurements by CT s at this current ,may exceed the set
current.Even 1% error in measurement at normal current
becomes 15% of In at initial charging current at 15 times
the In
| Is This Answer Correct ? | 0 Yes | 1 No |
What is the simplest formula to calculate the rotor diameter of a synchronous generator?
how to cal calculate capacitance in DC Circuit
How can transformer winding insulation be measured (Delta & Star Connections)?
What do you mean by 4.44 in this transformer equetion E=4.44 nfqm
oil cooled transformer
Q: How to calculate Transformer losses , tell us by Formula.
explain Xmer
1.How to calculate backup time from series connected battery of 12v dc with 26Ah for 2battery?
What is the maximum current carrying capacity for both copper and aluminium cables for 1sqmm?
what is the difference between STAR and DELTA connection and application wise how it can be utilizedd ???
in dc shunt motor if armature wdg is open then
what is the function of Droop CT and where it is used?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)