for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
Answers were Sorted based on User's Feedback
Answer / parth belani
Since the neutral of the star connected secondary is
already grounded through NER, there is no need to run a
neutral cable.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ramesh
there is no need of taking neutral point unless u need.Because mostly in 33kv Switch board you will feed 33/11Kv or 33/6.6Kv Transformers ,which will be mostly in (Dyn11 ior Dyn1) or to any other 33KV boards. Any how you are not going to take any motors load directly in 33kv.so it s not neccessary. but if you feed any star connection load in Primary you need to take neutral point.
| Is This Answer Correct ? | 0 Yes | 0 No |
It is not necessary to run a neutral cable as the same is
not requried for a 33 kV 3 wire AC system. But you need to
be cautious about the circulating/eddy current (since in
is a single core cable) which flows through the screen of
the 33kV cable. The voltage genrated by the circulating
current should be more than 130 V as per IEC standards. In
case of heavy circulating current the cable would get
heated up. You may do earthing of the cable only at one end
and leave it open at the other end. In case of a very long
cable with joints in between, mid point bonding is
suggested.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / indreswararo kota
for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
| Is This Answer Correct ? | 0 Yes | 2 No |
how is the incoming cable size calculated for a given current rating of a panel??
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
how i meggar value of 11kv alternator winding.and with meggar.
Why we say three phase voltage 440v.
Give a brief idea about Control circuit wiring in Substation...???
When and where resistance earthing is used ? How to calculate the time constant for earth fault
What is the Power factor of DC Power system ?
1)Explain why the cradle guard is used on railway crossing in overhead line construction?
In 90 kva alternator that produce the output voltage is 115(p-n),200(p-p) at 1500 rpms means what ampere it produced ?
lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???
what is reason in mv breaker the control supply voltage is dc not ac?
What types of testing in 11Kv Ht switchgeat during testing?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)