for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
Answers were Sorted based on User's Feedback
Answer / parth belani
Since the neutral of the star connected secondary is
already grounded through NER, there is no need to run a
neutral cable.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ramesh
there is no need of taking neutral point unless u need.Because mostly in 33kv Switch board you will feed 33/11Kv or 33/6.6Kv Transformers ,which will be mostly in (Dyn11 ior Dyn1) or to any other 33KV boards. Any how you are not going to take any motors load directly in 33kv.so it s not neccessary. but if you feed any star connection load in Primary you need to take neutral point.
| Is This Answer Correct ? | 0 Yes | 0 No |
It is not necessary to run a neutral cable as the same is
not requried for a 33 kV 3 wire AC system. But you need to
be cautious about the circulating/eddy current (since in
is a single core cable) which flows through the screen of
the 33kV cable. The voltage genrated by the circulating
current should be more than 130 V as per IEC standards. In
case of heavy circulating current the cable would get
heated up. You may do earthing of the cable only at one end
and leave it open at the other end. In case of a very long
cable with joints in between, mid point bonding is
suggested.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / indreswararo kota
for a 132/33kv transformer secondary is star and is
connected to NER. and from secondary a cable is running to
33kv swbd. since the cable is single core do i have to run
neutral cable also to 33kv swbd.???
| Is This Answer Correct ? | 0 Yes | 2 No |
What's an AVR? What's its purpose in Generators?
why two point starter,three point starter, four point starter cannot be used for A.C machines?
What is Nominal voltage?
Why in ESP Positive earthed
Is it possible to interlock between ACB & MCCB?
If the t/f capacity is 500KvA then what is Amps ratting of the main breaker.
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
How we can differniate the overhead lines feeded by hydro power stations & thermal power stations
what happen if we supply 220v dc suppy to the bulb or tube
Dear sirs, pls check this 4-20ma to RS485 module datasheet,pls guve me some suggestions. http://www.szsunyuan.com/sy/pro_more.asp?Productid=539 Thanks. E-mail:yunianjiang99@gmail.com
In stepdown transformer 11/415 volt two nos.(R & Y)HT side fuse is blown ,what will be voltage of ry,rb,yb in secondary side
What is Synchronization of generator,where and how it is achieved.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)