Answer / dinesh lokhande
Let us first understand type of bushing.
Bushings for 132 kV class transformers are generally OIP
(Oil impregnated paper)bushings. However before charging
transformer air release to be done from tranformer tank and
bushings to release trapped air during oil filling. If in
any part of bushing air is trapped then air gets ionised
and provides a path for voltage beakdown resulting in
brsting of bushing due to high voltage stress in bushing.
Some other reason may be dielectric brakdown due to ageing.
Additional information.
Capacitance Tan delta test for OIP bushings can provide
readings of capacitance and tan delta which are indicative
of bushings deilectric health.
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / sathishbabu t
132kv(hi voltage,low current) has less rated current
capacity bushings, if we applied low voltage 6.6kv(low
voltage,hi current) bushing cant withstand hi current.
hence bushing burnt.
Is This Answer Correct ? | 12 Yes | 5 No |
What happens if a three phase induction motor is suddenly single-phased while running? Which type of winding connection will be affected?
22 Answers B4S Solutions, DRDO, FACT, SL Electricals,
in transformer star connection with neutral are shorted. is there is any effect.
If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to alternator windings??????????
EXPLAIN THE FOLLWING: (1) BANDWIDTH (2) SELECTIVITY (3) RESONANT FREQUENCY (4) CURRENT MAGNIFICATION
WHAT IS REMOTE CONTROLLED DG? WHAT IS DIFFERENCE BETWEEN REMOTE CONTROLLED DG & NORMAL DG SETS
1-What is the difference between absorption factor and polarization factor in insulation resistance test in transformers? and why we inject until ten minutes to get polarization factor?
what is dyn 11
AVR
Explain dc generator with its types?
what is sevice settings for mccb?How can be it setted?
how to change the load sharing between two synchronized identical alternators when both are running with Diesel engine? assume both are feeding to same feeder?
in CNC reference how to take? what kind of input give to the servo amplifier?