how system fault level is calculated?
Answer / vinay harit
if we known the pesentage of impedance then by using this
formula we can calculate the fault Lavel.
fault lavel in MVA= Rated KVa/% of Impedence
OR
Fault Lavel= 1.732xFault Currentx Rated Voltage
Is This Answer Correct ? | 5 Yes | 0 No |
What is the role of the 50 STUB protection at a GIS 400KV substation with SIEMENS protection relays?
what is negative phase sequence
how ct burden,magnetising current,ratio and knee point voltage are related & derived
How can we find the breaking capacity of a Load breaker switch (LBS) fed from 11 kv supply??ex:50KA, 26kA etc???detailed step vice answer pls.
megger how much voltage will produce ?
how can a transformer test by megger?
sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formula ?
What is the function of semicon in 33kv ht cable ?
if the magnetic lines can pass through a vaccuum area
While miss missed name platform fo electric motor how to calculate simple fourmul,?
What are the methods/types of distance protection schemes used in transmission system?
In my 3 phase 4 wire electrical system N to earth voltage is 0.08 is it ok What is standard for it ?