what is first pole to clear factor ?
Answers were Sorted based on User's Feedback
Answer / pawar shyamkant sitaram
It depends upon the system power frequency voltage before
the fault appearing on first pole to the volage appearing
across the heathy poles after clearing the fault. The value
of first pole to clear factor is mainly decided by the
sytem grounding & ratio of zero seq.impdence to positive
sequence impedance.
Is This Answer Correct ? | 13 Yes | 3 No |
iF THE THREE PHASE FAULT NOT INVOLVING THE EARTH THE
VOLTAGE ACROSS THE CIRCUIT BREAKERPOLE. FIRST POLE CLEAR
105 TIMES THE PHASE VOLTAGE IN 3 PHASE AC CIRCUIT BREAKER
ARC EXTINTION IN THE THREE POLE IS NOT SIMULTENEOUSLY AS
CURRENT IN THREE PGASES ARE MUTUALLY 120 DEGREE OUT OF
PHASE. HENCE THE POWER FREQUENCY RECOVERY VOLTQAGE OF THREE
PHASE IN WHICH ARC GETS EXTINGUISHED FIRST IS ABOUT 105
TIMES OF PHASE VOLTAGE.FIRST POLE TO CLEARE FACTOR IS THE
RATIO OF VOLTAGE BETWEEN HEALTHY PHASE TO FAULTY PHASE TO
NORMAL PHASE VOLTAGE.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / sudipt jena
Actually the voltage rise due to TRV is 1.2-1.5 times that of phase voltage.And this is happened due to the 120 degree phase shift of 3 phase current leading to interrupt of current at different instants.
Is This Answer Correct ? | 0 Yes | 1 No |
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
why induction motor speed is decress with increase in load? how synchronous motor speed is constant?
IN HT MOTOR HT REFERS TO HIGH TENSION OR HIGH TRANSMISSION?
if we have 320KVA Genset kindly advice how much load we can put it.
I am having a 1500 KVA transformer whose secondary current is 2086A and my connected load is 1000 KVA, I am having 400 KVAR APFCR for PF improvement what ratio of CT should i install in LT EB Bus to get optimum PF improvement?
What are the disadvantages of hydropower?
I want to know if it is possible to use Variable Frequency Drive to reduce the current required for starting a motor?
how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?
pls send me some question and answer for rrb railway interviw related 2010
Define Current Transformer? Working & TYpe's Of C.T.
What is difference between ct&pt transformers?
why voltage coil in wattmeter called as pressure coil why the pressure term is used in wattmeter?