What could be the problem if two power transformers trip on
stand by earth fault at same time
Answer / k.prakashchandra
If the point ct neutral earthing is in the path of earth
fault current, there is likelihood of tripping of standby
transformers on earth fault.
| Is This Answer Correct ? | 1 Yes | 0 No |
Transformer cores are laminated in order to A simplify its construction B minimize eddy current loss C reduce cost D reduce hysterisis loss
what is kondo syatem in eletrical traction
what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line
i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star connection at both side.but it have another thied winding tertiary winding.what is used of this winding. pl tell me
How do i calculate sizing of transformer on didstrubution load for high rise building.What should be MVA Rating of MV Panel feding by 122 kv.
why CT out put is 5 what ever the primary current.
Is the theorem applicable to ac sources?
how actually an anti pumping device works? what is the operational principal?
working principle of oil startar
Why LVDT have secondary windings connected in differential 1. Higher out put 2. Based on the out put voltage-/+, helps to identify the direction of displacement 3. To establish a null/ reference point
What is the difference between bushing and insulators.? what is the creepage distance?
Why we use Capacitor in Single Phase Induction Motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)