How to calculate KW what is the formula for KW.
Answer Posted / manoj kumar
for single phase it is-
average voltage x average amp. x power factor (0.85)
____________________________________________________
1000
for three phase it is-
average voltage x average amp. x power factor (0.85) x 1.732
____________________________________________________________
1000
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
How do i right a ladder diagram that has 1 actuator that performs a full stroke followed by a half stroke
Whether should be the oil level in OCTC transfomer? It should be upto winding immersed completely or should be upto tap changer s/w? How it will affect the performance of the transformer. Rating may be 33KVA
What is the formula for calculating no-load current?
how to find the Motor,s insulation Power?
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
What are the various kind of cables used for transmission?
how to calculate the Neutral transformer impedance?
Please, if 1kw is equal to 1.25kva; how then do I know how many kva in 7.5kw?
As we use capacitor bank in 3ph ckt to improve PF, can we use capacitor in single ph domestric use, in house we have Fan,Mixer,electric cooker,iron,tube choke they also lag the system,because it is inductive load. if it is possible to improve PF of single ph system-- if yes- type of capacitor to be used,connection diagram, working in detail. if no-- list it.
CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS
What is tan delta & PPM in transformer? and whats its IS value?
State the other types of Air Conditioners?
I want single line diagram for AMF & DG syncronizing panel
Purpose of providing neutral isolation panel for parallel operation of diesel generator
why core is useful for a transformer ?and also in its operation ?