transformers parts & function of each parts
Answer Posted / saravanakumar
primary winding,secondary winding and transformer core are
all the main parts of the transformer.
the supply voltage is connected to the primary
winding, the load is connected to the secondary winding and
in the transformer core only the magnetic flux path will b
established..
in power transformers(used for transmit the heavy
voltages to the grid) on load tap changers used.. but in
distribution transformers off circuit tap changers are
used.
there is another type of transformers called auto
transformers in which part of the primary winding used as a
secondary winding.
buccholz relay s used for the transformer protection.
| Is This Answer Correct ? | 322 Yes | 59 No |
Post New Answer View All Answers
What is the working mechanism of OLTC in Power Transformers????
What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.
physical identification of HT & LT panel
What are gain margin and phase margin?
Dear all, I just want to ask an expert on this forum for some insights. For the magnetic balance test, when applied voltage on a Delta-Star transformer e.g. Dyn11, the following relationships apply for HV side: 1. H1-H2 = H2-H3 H3-H1 2. H2-H3 = H3-H1 H1-H2 3. H3-H1 = H1-H2 H2-H3 For the LV side also: 4. X1-X0 = X2-X0 X3-X0 5. X2-X0 = X3-X0 X1-X0 6. X3-X0 = X1-X0 X2-X0 Is there a similar pattern for Y-d, Y-Y, D-d? And how about Y-z, D-z, Z-y transformers? I've tested a YNzn5 transformer and for LV side I don't see the pattern. In this particular case I got for LV side the following (see values below): H1-H0 H2-H0 H3-H0 X0-X1 X0-X2 X0-X3 128.0 119.9 7.2 29.2 13.3 15.8 70.7 128.4 59.2 23.4 22.0 3.6 7.2 120.1 128.1 13.4 29.3 15.8 What is the relationship here for LV? For row 1 I see the relationship, for row 3 I also see but it's shifted, but for row 2 I don't see such relationship. Any suggestions, answers, someone?
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
Dear all, how we select the cable size according to current with or without including different correction factor , is there any direct method for sizing of cable...
how technical is calculated in 11kv line and lt line
how to control the speed to switched reluctance motor
if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
What is the ideal position cooling fan inside the dc motor?
what is the benefit of floating our DC source? if i have two floating DC source of which 1 has a ref voltage of -21VDC and the other of -18VDC. can it be connected in parallel to share a common ref voltage? if not, how do i make both sources to be of common ref voltage? tks
In single phase capacitor motor, if the motor rotate reverse direction then how much power will be consumed by the motor and why?
After completing iti in electrician, how can i get certificate of electrical supervisor? What ia requirements. For it?