what is the purpose of battery tap voltage.
Answers were Sorted based on User's Feedback
Tap votage is from the battery in 75-80% position so that
this volage is equal to the normal (float charge) voltage
of the battery set, when boost- charging is going on ,so
that DC supply voltage to the appliances is not as high as
boost voltage which could be 30 % more than the rated
volage of the battery set
Is This Answer Correct ? | 23 Yes | 1 No |
Answer / prasanta kumar das
During boost charging total set of battery set on high
voltage charging.To save the 220v DC connceted system from
above boost charging voltage,a tapping done from the 80%
cell,from where we can get 220v DC.
Is This Answer Correct ? | 5 Yes | 0 No |
What is the value of 3 phase voltage?
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
Transmission line design. Say, I have a 1MVA generator and 2 transformers that will have the same load. What would be the proper rating of the trasformers? Is it safe to say, that I will simply divide the total rating of the generator?
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
what is full wave bridge?
how to interlock 3 incomer-ACB,1 buscoupler ACB,... pls answer this question and if possible send me the ckt diagram..haifriends2910@gmail.com
who is invented transforner (230v).......
Squirrel cage induction motor has constant A slip B stator current C rotor resistance D speed at all load
(1)The demand for electricity , the amount of renewable generation available, the amount of fossil fuel generation available and the cost of the fossil fuel generation are shown in table below period(hrs) demand(MW) renewable (MW) fossil- fuel(MW) cost of fossil fuel(MW) 00.00 - 01.00 2000 1800 2000 30 01.00 - 02.00 2300 2500 2000 30 02.00 - 03.00 2500 2700 2100 45 03.00 - 04.00 2900 3100 2100 50 04.00 - 05.00 2700 2600 2500 45 05.00 - 06.00 2400 2000 2700 50 06.00 - 07.00 2200 1800 2000 36 07.00 - 08.00 2100 1600 2000 36 Assuming that the renewable generation incurs zero cost, determine an optimal generation schedule(specifying the amount of renewable generation and fossil fuel generation used in each period, the cost for each period and the overall cost for 8 hours.)
why all selected supply voltages are multiple of 11.i.e440,11 kv,33 kv,66 kv,110 kv etc
What happens to a motor if it is connected in Delta connection
1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?