A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?
Answers were Sorted based on User's Feedback
Answer / parul
Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.
After considering all above checks you may do the earthing
of neutral point in your load.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / velusamy
check the overall earth pit resistance value and it
should be less than one ohms
Is This Answer Correct ? | 1 Yes | 1 No |
It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the avr
6 Answers ArcelorMittal, Heidelberge Cement,
what is the basic construction diffrance between servo motor ans sqiralcage induction motor
what is the principal of star delta starter?
why transformer rated in KVA not in KW ? we know that W= v*i
why is neccessary Tap changing of power transformer with in a certain time
in a dc motor we supply current only to the armature conductors,from where is the field winding gets excited then??
what is the range of maximum DOL and SDS can be use for pump and fan application
we know that dc motors are more superior then three phase induction motors in torque generation though they are not much used in industries why?
Convert a star connected network into a delta connected network.
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
we touch other end of the tester supply, why do not get shock?
hi i have applied for lic of india south cenrtal zonal ,hyd. i didnt get hall ticket till now.let me know how can i get form internet