A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?
Answers were Sorted based on User's Feedback
Answer / parul
Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.
After considering all above checks you may do the earthing
of neutral point in your load.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / velusamy
check the overall earth pit resistance value and it
should be less than one ohms
| Is This Answer Correct ? | 1 Yes | 1 No |
It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.
| Is This Answer Correct ? | 0 Yes | 0 No |
Is there any type of starter for DC motor other than two point,Three point and Four point starters?
why star 2 delta or delta to star preferred mostly then star to star and delta to delta ?
Totally how much power will be consumed in 1 hour cotinuous running of electric train engine?
PLS MENTION QUESTIONS ASKED IN IOCL INTERVIEW FOR ELECTRICAL EGG??
How can we prevent the (Home)inverter supply flow to the main supply line?
what is the meaning write of AC1,AC2,AC3 .....power contactor
How Diesel Generator start ?
0 Answers ITC Infotech, Voltech,
rajha power sector details
What is IDMT relay how it works.
3 Answers Electrotherm, Sulzer,
purpose of flux relay for turbo generator in power plant
at what base you will tell the direction of rotation of dc motors and generators?
explain impact of tariff on energy management..? and what is ABT tariff
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)