if you short the any 2phase(R,Y,B),why fuse get blown?
Answers were Sorted based on User's Feedback
Answer / senindra123
when two phases shorts it means short circuit. so high
current wil flow through fuse. so its get blown.
Is This Answer Correct ? | 39 Yes | 0 No |
Answer / shakir
when we short two phases the resistance between them is 0 and
current goes to infinity (I=V/R). such an infinite current
when pass through a fuse,the fuse gets blown.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / vasudeva rao
two pase gets shorted means (L-L fault) in this fault phase
currents are very high
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / bmw6633@gmail.com
because it double the voltage which leeds high resistence
then the fuse should blowen of.
Is This Answer Correct ? | 4 Yes | 12 No |
Answer / bmw6633@gmail.com
because it double the voltage which leeds high resistence
then the fuse should blowen of.
Is This Answer Correct ? | 4 Yes | 12 No |
Based on what the rating of machines are provided??(ANswer should in single word)
19 Answers Asian Paints, Bhel,
Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?
At light load transformer efficiency is less because A secondary output is low B transformer losses are high C fixed loss is high compared to output D copper loss is small
Does the isolator has a making capacity????????
How over load relay works.
What are the types of circuit breakers ?
for opening electrical shop, tips needed.
IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
Why transformer use to generator neutral earthing purpose ?
how can you calculate the value of external resistance inserted in a slipring industion motor? (eg. 110 kw / 990 rpm/50Hz/stator v-415/stator Amp-195/Rotor V-440/Rotor amps- 151.)
Comparision of Air break circuit breaker, SF6 Circuit breaker and vacuum circuit breaker.