Answer / pooja
width of column is required for many aspects of design of,
isolated footing
1 for calc. of load of column
2 for providing dimension of footing in the same ratio as
that of the column
3 for B.M & S.F calculation also max. dis is taken by
deducting dim. of col.
Is This Answer Correct ? | 48 Yes | 5 No |
Answer / minaz akbar
depth of the footing is decided by punching shear/diagonal
shear and the bending moment..... the max depth is given by
punching shear.... and all the three methods depend on the
width of the column. the thickness of the footing should be
able to resist the tendency of the column to penetrate and
punch a hole through the foundation block.
Is This Answer Correct ? | 35 Yes | 0 No |
Answer / d.ramachandran
IT SEEMS ANSWER BY MR MINAZ AKBAR IS CENT PERCENT CORRECT
AS THE FOOTING IS DESIGNED FOR PUNCHING SHEAR AND DIAGONAL
SHEAR THE PERIPHERY OF COLUMN IS TAKEN FOR CALCULATING
PUNCHING SHEAR......BENDING MOMENT MAY VARY DEPENDING ON THE
THE OVERHANG PORTION OF THE FOOTING AND IT MAY NOT BE A
FACTOR FOR WIDTH OF COLUMN
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / dr.eng.mustefa
moment at the face of column is main for footing design..
even tapering may not be needed as it is done only to save
concrete as steel is required in free end
but in case of deep footings more than 1.5 feet double
reinforcement is given at top and botttom
,you know that punching force and wide beam forces are
considered; by leaving the place covered by the column
dimenshions,and taking critical sections arround the
footing. I think it is enough Answer.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / d.ramachandran
do u mean we can take moment for the whole width of footing
moment at the face of column is main for footing design..
even tapering may not be needed as it is done only to save
concrete as steel is required in free end
but in case of deep footins more than 1.5 feet double
reinforcement is givenat top and botttom
i hope ihave explained correctly..somebody may pl answer to
my mail
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / vkadian
after that we can design dimensions of footinf.
Is This Answer Correct ? | 10 Yes | 11 No |
Answer / d v n potharaju, hyderabad
Firstly size of the column is required for calculating the
max bending moment occuring at the face of the column i.e
for calculating the depth based on B M cretiera.
Secondly size of the column is required for calculating
the max punching shear force that has to resist i.e for
calculating the depth based on punching shear cretiera.
Out of the above II cases max depth has to considered.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / saravanan
THE FOOTING IS TO DISTRIBUTE THE LIVE LOAD $ DEAD LOAD FROM
COLUMN,BEAM,SLAB & WALLS . THE TYPES OF LOAD ARE TRANSFER TO
THE FOOTING SO THE DEPTH OF THE COLUMN IS CONSIDERED...
Is This Answer Correct ? | 1 Yes | 5 No |
how we can calaculate cutting lengh for stiruups 6mm dia . column size 20 cm x 30 cm, cover 20mm
how much quantity of steel required for 1sqmt area?
4 Answers Jade Software, Samsung,
How to calculate the length of chairs provided to support the top rebar in concrete foundation
what is a exact size of a cube?
why provide water stopper in costruction joits
how much steel is required for 1 sqft of slab
granite tiles laying 60/sq ft.how to convert in sq mt,what is the mltiplying value.
how much weighs a square feet of slab of 5 inches thick
What is the tensile strength of marble?
In site how we can identify one way slab and two way slab?
11 Answers Parth Constructions,
Explain the mechanism of cavitations in pipes and drains?
1) is maximum size of aggregate ristricted to 20 mm for M- 50 grade concrete? If yess or no code the authority?