Could anybody tell how much amps will a single input to plc
will consume?
Answer / carl_ellis
The spec sheets on my desk have these specs:
for an AC voltage digital input:
2 mA nominal @ 230 VAC, 50 Hz
for a DC voltage digital input:
2.3 mA @ 12 VDC
6.9 mA @ 24 VDC nominal
for a dry contact digital input (internal 15Vdc source):
2.6 mA nominal
Interviewees should be able to convert from milliamps to amps.
Normally, power (watts) is 'consumed'.
Current (amps) is a 'draw' on the power supply.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
what are the following documents comes under loopchecking
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
Good Evening all.My question is - For a feed water line to an equipment if i need to measure the flow we will use orifice /magnetic/vortex depend on cost/spec.If i need to measure a ''Alarm''signal and ''Interlock'' from one point i think we can use orifice type in one location with 2 different tapping points - one for alarm and one for an interlock to flow valve..If in case i need to have both these signals(Alarm & interlock) from magnetic flow meter,is it possible??will 2 seperate sensors will be located inbuilt r we can program it ??..i thk we can have one transmitter with these 2 signals...need to know any technical issues are there?pls clarify
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
What is the loop calibration? Which instrument used to loop calibration and how?
whether radar level transmitter is applicable for the open tank
Absolute pressure is 700psi,what will be the gauge pressure?
Why we use 4 to 20 mA, (This is International Standard) instaed of this can we use 4-16, or 4-24 or 3- 15 or any other range
Pls.could any one Clarify the following with an example. 1.At What condition Close on Rise and Close on Fall Pressure Switch contacts are used. 2.If Pressure is abnormal as per set pressure,if connecting Terminal of pressure switch breaks,how the voltage extends to Relay base. 3.Are these contacts come under fail safe philasaphy.
what do u mean by compensation n pid tunning?in pid tunning what you tunned?is it possible 2 tune p i d
Which softwere is required to communicate the S7-300 processor
Dead weight tester & comparator for calibration , which is more accurate , what is the application.
1 Answers Bapco Bahrain Petroleum Company,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)