Could anybody tell how much amps will a single input to plc
will consume?
Answer / carl_ellis
The spec sheets on my desk have these specs:
for an AC voltage digital input:
2 mA nominal @ 230 VAC, 50 Hz
for a DC voltage digital input:
2.3 mA @ 12 VDC
6.9 mA @ 24 VDC nominal
for a dry contact digital input (internal 15Vdc source):
2.6 mA nominal
Interviewees should be able to convert from milliamps to amps.
Normally, power (watts) is 'consumed'.
Current (amps) is a 'draw' on the power supply.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
when a magnet is heated?
GWR radar transmitter working principle?
can u please give the exact ckt explaination of AC Drive related to industries.
tell about various protocols used in different plcs
What care will you take in the installation of control valves,SCADA,DCS and FOC in Oil and Gas Project?
WHAT IS AN INTERLOCK SYSTEM ?? HOW THEY WORKs ?? WHERE IT IS USED ??? MAINLY ??
2 Answers TATA, Tata Steel Limited,
how u measure flow?orifice measurement?why all ft in square root?
how the transmitter send MA?
Isometric drawings are generated during _________________ phase of a project
Which products are available in the Mass Systemswitch and System Manager AC range?
where the use of direct action control valve?