Please let me know when replacing electromechanical
Relays for protection of generators with sr489 multilin
Relay, then there is no need to use 86 master trip relay
Too. I am wondering this multilin relay has no contact to
Stop breaker reclosing as 86 does
The electronic relays do not have heavy duty contacts and they are usually self reset. Tripping relay is required to take high trip currents and they are to be reset . Otherwise the contacts of e- relays will burn out and breaker may close without clearing fault . In addition , a back up EM relay may be required
Is This Answer Correct ? | 0 Yes | 0 No |
why power not passes in plastic and rubber material
In case of power/distribution transformer what is percent impedence?
"What is the difference between voltage and potential differnce?"
design of IGBT firing circuit for 11KV
what is pf. how to calculate capacitor bank value to maintain unity pf.
18 Answers JH, Saint Gobain, Supreme Treves,
What is the power ratio between power in Star and Delta circuit?
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .
what is the Knee point Voltage?
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
long form of CT
3 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
How to calculate cable size? How to O&m of vcb?
Is it possible to measure the voltage of a battery from a single terminal?