The neutarl to earth voltage in system is 7volts on
Electricity power but it lowers to 1.3volts when load
transfered to DG power.what may be the reason.
Answers were Sorted based on User's Feedback
Its depends upon healthyness of earthing and nuetral. for
good earthing there should be minimum voltage drop between
earth and nuetral.
So from above example its clear that neutral or earthing of
Transformer not proper. It can be check by earth tester
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sridhar
loose connection in Earth Bus must be checked , Often
Earthing is neglected
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pillay
If your intake is small and direct from the electric board
than it is normal ,that means the neutral of the power
supply board is is not so good, but when you transfer to DG
the neutral and earth which is within your control is
better earthed. If your intake is HT and through a
transformer than likely your transformer neutral earthing
or the neutral route is in question.
Is This Answer Correct ? | 0 Yes | 0 No |
why would amp draw on neutral wire be as much as amp draw on the hot leg.
While testing the value of the resistance for the earthing rod, two auxillary rods are connected to the earthing tester.What is the working function of a earth tester?
IF I USED VVVF DRIVE IN FAN APPLICATION MOTOR IN 6.6 KV ( 700 KW) MOTOR & DURING NORMAL RUN OPERATION TIME IF RPM SUDDENLY REDUCE IN MOTOR BY DRIVE(E. MOTOR RPM REDUCE SUDENLY 687 TO 550 RPM) WAHT WILL BE HAPPEND IN DRIVE
i have 400/230v transformer and didnt done the neutral eatrhing. i connected one lamp to one phase and neutral to the earth. but the lamp is not glowing. again i connected neutral to earth and repeated the same. then the lamp is glowing. in the first condition i tested with a line tester also, at that time the tesrer is glowing what is happening i dont know can any one help me?
How to calculate LT XLPE CABLE for 11 kv / 433 v , 1000 kva oil type transformer system?
Explain difference between stand by earth fault and residual earth fault protection?
why we are 0.8 power factor only?
What is difference between stable and steady?
How will you explain transformer action in case of 3-phase induction motor?
Can anyone please give me the parameters , formula needed to calculate the circuit breakers for building services.Thanks
what is the importance of Partial Dischage test for Electrical Equipments
can i use the six sigma method which is used in management area, in state estimation of power systems?