What will happen if 60 Hz rated transformer is connected to
the supply of 50 Hz say 415 V (3-phase) step up to 3.3 kV...??
?
Answers were Sorted based on User's Feedback
Answer / himanshu kumar singh
transformer will work at 60 hz without being
overheated...but the core losses will be more.
| Is This Answer Correct ? | 20 Yes | 4 No |
Answer / rohan
induced voltage is dependent on frequency. so if x'mer designed 4 60 hz runs on 50 hz then o/p is a little less than 3.3kV
| Is This Answer Correct ? | 2 Yes | 1 No |
what are the main parts of UPS what is the function of that?
23 Answers Apollo, HCL, Liebert, Royal Furnishers, Tech Mahindra,
Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp. ?
Which motor isused in indian railway system?
in power station power measuring unit is KW but in transformer is KVA why?
can i connect REF and Differencial relay in 1 CT core for transformer protection?
What is differnce b/w tie breaker and bus coupler?
what is the difference SCR & TRIAC?
OHMS Law is only applicable for ac or dc or both circuiT?.
whu the transformer noise during running condition?
where the lexical paramater will use in fron end?
what is the use of Reactive power in power system?
Iwould like to know barc interview questions
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)