What will happen if 60 Hz rated transformer is connected to
the supply of 50 Hz say 415 V (3-phase) step up to 3.3 kV...??
?
Answers were Sorted based on User's Feedback
Answer / himanshu kumar singh
transformer will work at 60 hz without being
overheated...but the core losses will be more.
Is This Answer Correct ? | 20 Yes | 4 No |
Answer / rohan
induced voltage is dependent on frequency. so if x'mer designed 4 60 hz runs on 50 hz then o/p is a little less than 3.3kV
Is This Answer Correct ? | 2 Yes | 1 No |
how to calculate current and voltage in a same circuit?
what will happen at the time of CT saturation?and what will be the Relay's function at the time of CT saturation?
What is the difference between PLC and Embeded system
Question about ct secondaries connections?
what is the necessity of neutral in 3 phase system?
how to set the transformer differential relay
Calculate the demand in KVA for a three phase 440V power source drawing 1100A current
What's the difference between non break power supply and non break non short break power supply
What is force on a conductor in a magnetic field ?
WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION?
circuit breaker is ...............connected with circuit
The windings of a transformer are divided into several coils, because?