What will happen if 60 Hz rated transformer is connected to
the supply of 50 Hz say 415 V (3-phase) step up to 3.3 kV...??
?
Answers were Sorted based on User's Feedback
Answer / himanshu kumar singh
transformer will work at 60 hz without being
overheated...but the core losses will be more.
Is This Answer Correct ? | 20 Yes | 4 No |
Answer / rohan
induced voltage is dependent on frequency. so if x'mer designed 4 60 hz runs on 50 hz then o/p is a little less than 3.3kV
Is This Answer Correct ? | 2 Yes | 1 No |