Sir
Power transformer :- (in generating station)
Alternator terminals side - Delta
HT transmission line side - Star
Why?
Answers were Sorted based on User's Feedback
Answer / anup mohan
I could not understand the question clearly... but.. in generating n transmitting the terminals are in delta... as we need only 3 phases..... but at the other end.. i.e on the distribution end.. the connections are in star/wye... thtas ca.. in addition to the 3 phases we need a neutral... we ve neutral conection only in star and not in delta
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / nagarajan
Example 15mva,220/132kv
Star 220kv here phase voltage =line volatge/1.732=127kv
delta 11kv here phase voltage =line volatge.
Because star side we have neutral ,a.insulation cost less and 127kv insulation is sufficient but in this delta we require 132kv insulation.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kc
To reduce the fault level
The fault on primary side ie Y (LLG)
Will reflect as a LL Fault
So fault current level will b less
No zero sequence current ll b appar on d secondary side
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhim kumar yadav(l&t)
bcz in delta side voltage is more compare to star side. so
insulation cost is very-very high in delta side compared to
star side.therefor, we keep always star connection in HT
side
| Is This Answer Correct ? | 2 Yes | 3 No |
tell me any book for current n potential trasformer with full knowledge ?
Why in 6 KV XLPE cable termination kit used and why not in 380 V xlpe cable same is not used
is that any software calculator to calculate the size of cable
my 10 hp submersible pump is tripping when connected through ELCB.I have checked the megger value of the coil's with body.It was found to be 0.2mega ohm.that is leakage is there.But when connected to mccb it is not tripping.no leakage current in the motor.Is it safe to connect to mccb? what are the problem's will arise if future?also tell me in ELCB no neutral is connected to motor.than how ELCB was working?
if we install two earth pits with a clear space of 5m without any interconnection,by checking the digital multimeter will it show continuity between earth pits? If so what would be the approx. value
WHEN THESE TRANSFORMERS WINDINS CONFIGURATION ARE USED? SPECIALLY EXPLAIN REGARDING STEP UP AND STEP DOWN KEEPING IN MIND.AND REGARDING LOAD ALSO. a.star to delta b.delta to star c.delta to delta d.star to star ALSO EXPLAIN WHY V USE 415/415 TRANSFORMERS IN TUBEWELLS?
what is the difference between delta delta and star delta connection transformer? why we use delta delta transformer since it need earthing transformer for grounding?
what is main parts of alternator.
Why the moulded plug comes with domestic appliances instead of assembled plug like anchor, Vinay 5/15 A.
What is the basic principle of welding process?
Hi Recently I got one formula that is Impedence of Xformer = Rated KVA/Root 3 * secondry voltage OF Xformer. Is it Right??????
What will happen if i connect the delta winding motor to star input.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)