what is the diff of mcb and mccb
Answers were Sorted based on User's Feedback
Answer / desingurajan
MCBs are miniature circuit breakers with optimum protection facilities of overcurrent only.These are manufactured for fault level of up to 10KA only with operating current range of 0.5 to 63 Amps (the ranges are fixed), single,double and three pole verson.These are used for smaller loads -electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection facilities of overcurrent, earth fault.it has a variable range of 50% to 100% operating current.They can be wired for remote as well as local operation both.They are manufactured for fault levels of 16KA to 50KA and operating current range of 25A to 630Amps.They are used for aplication related with larger power flow requirement.
Desingh
RAjapalayam
Is This Answer Correct ? | 16 Yes | 0 No |
Answer / kadher.304
mcb its thermal operated and use for short circit rating of
mcb 63amp(max)
mccb is thermal operated for over load current and magnetic
oprataion for instant trip in short circuit condition.rating
of 63amp(9min)
Is This Answer Correct ? | 7 Yes | 1 No |
What is the difference between ground and neutral ?
Which companies are into the project management of construction of power transmission line?
what is the value of voltage & current lightning during rainy season.
why the neutral of power transformer is always earthed?
how many synchronous motor are there in any power plant
How transformer winding & oil gets heat.
What are the methods/types of distance protection schemes used in transmission system?
what is the formula of starting current of 3phase and 1 phase motor???
While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens
what is the condition for YnD11
Draw a SLD of HT distribution EB grid up to users Transformer?
minimu size and length of gi earth pipe