Ok I think I understand what you are asking. In most SMART
transmitters you have a digital indication on the
transmitter and you want to change what is displayed on this
indicator. You also said that you have changes the unit of
measure inside the transmitter with the HART, and this also
changed the UOM that is displayed.
There is a different parameter that you need to modify to
change the display. The parameter is normally something like
"set disply" or something like that.
Be aware that it will only display UOM or percentage or
display a switching between the two. What ever you have set
your UOM to inside the transmitter, will be displayed on the
indicator as the UOM. You cannot set the UOM to mmH2O inside
the transmitter and then display mBar on the display.
Also note that for a level application this display is
normally set to percentage and not UOM. If the operator look
at it he needs to see % level and not mm level. In a
pressure, flow or temp applications you want this display to
indicate UOM again.
Good luck
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / omer baosman
First of all,parameter's which need to be diagnostic in
transmitter with any of communicator will be in percentage .
Like for flow eg: Kgs,temp eg:cc fh level eg: % ,pressure
psi or bar.
Is This Answer Correct ? | 0 Yes | 1 No |
I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
How to calculate the flow rate in Vortex flow meter?What is K factor?Can you give me an example calculation to understand the same as better?
Explain the difference between the types of input variables plc?
can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).
What is the Difference between E/P Positioner and I/P positioner in a control valve? In which applications the respective positioners are used in?
What is difference between differential pressure & delta pressure?
I want to apply for the universities in US,but i got the GRE score of (650+300=950)TOEFL 69/120.Is this score sufficient for applying universities please i am married i need to go to US because my husband didn't get H1 yet.please send me suggestion
How hart protocol can be connected with control valves?
What is the difference between ROM & RAM .
in which mode of the zener diode act when load voltage is approximately constant
i have been asked by QAFCO to appear for interview for thy post of Instrument Designer(INTOOLS)..i m engineering graduate with 5 years exp. in design engineering.Will this job profile suit me??i need all ur help n suggestions for thy same?
What is the compensation of thermocouple