IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB)
USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO
ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE
THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART
COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
Answers were Sorted based on User's Feedback
Ok I think I understand what you are asking. In most SMART
transmitters you have a digital indication on the
transmitter and you want to change what is displayed on this
indicator. You also said that you have changes the unit of
measure inside the transmitter with the HART, and this also
changed the UOM that is displayed.
There is a different parameter that you need to modify to
change the display. The parameter is normally something like
"set disply" or something like that.
Be aware that it will only display UOM or percentage or
display a switching between the two. What ever you have set
your UOM to inside the transmitter, will be displayed on the
indicator as the UOM. You cannot set the UOM to mmH2O inside
the transmitter and then display mBar on the display.
Also note that for a level application this display is
normally set to percentage and not UOM. If the operator look
at it he needs to see % level and not mm level. In a
pressure, flow or temp applications you want this display to
indicate UOM again.
Good luck
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / omer baosman
First of all,parameter's which need to be diagnostic in
transmitter with any of communicator will be in percentage .
Like for flow eg: Kgs,temp eg:cc fh level eg: % ,pressure
psi or bar.
| Is This Answer Correct ? | 0 Yes | 1 No |
units for vibration in power plant
what is difference btween rotameter and orifice plate?
Tyes of interface level measurement and how to use that technique for interface level measurement,
What are the automatic controller MODES?
What is the use of control cable?
for what purpose strain guage is used?
How can measure flow in oil line?which type of transmitter is generally used?
How can we test a bently nevda 3500/42M accelerometer monitor card by simulating it with test equipment?. what king od of signal (milli volts or volts or or resistance ) we should feed in the terminals of the card?
Generally in which location ( JB or IO card or DCS) the thermocouple compensation is done.Also where they measure the atmosphere temp ( for compensation) in JB OR DCS panel? How they compensating that atmosphere temp? is any circuit for that ( like in rtd wheatstone bridge)?
(1) In turbine, what does term CDP, NI, NH, HSSOC, means. (2) What is the purpose of LO overhead tank in turbines.(3) An equipment is certified for EEX, IA, IIC,T6, what do you under stand by this.(4) what is SURGE, and how it is prevented, what is the purpose of bypass valve across AS valve.(5) Give 2 application of quartz crystal used for process parameter measurement.(6) what is meant by cold float of compressor shaft. (7) state four different types of flow measurement. For gas flow measurement mmscfd is the common unit. Expand the unit and specify significance of word S in the unit.(8) what is meant by Gap voltage, in vibration measurement. Normally how much Gap voltage is set and state the reason.(9) what will the new flow factor if D/P transmitter is Re-Ranged from 25” wc to 50” wc.(10) what is the usage of QDV & Volume booster.
please can anyone tell me in detail, what's mean by open loop and close loop?
Somebody tell me in what way i need to prepare for csio pgrpe(adv instrum eng)interview?what all the quest can i expect?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)