Answer / e mohana priya
A basic liquid sizing eqtn.. is as follows:
Q = C
V
∆P / G
(1)
where:
Q
=
Capacity in gallons per minute
C
v
=
Valve sizing coefficient determined experimentally for
each style and size of valve, using water at standard
conditions as the test fluid
∆
P
=
Pressure differential in psi
G
=
Specific gravity of fluid (water at 60°F = 1.0000)
Thus, C
v
is numerically equal to the number of U.S. gallons of water at 60°F that will flow through the valve in one minute when
the pressure differential across the valve is one pound per square
inch. C
v
varies with both size and style of valve, but provides an
index for comparing liquid capacities of different valves under a
standard set of conditions.
To calculate the expected C
v
for a valve controlling water or other
liquids that behave like water, the basic liquid sizing equation
above can be re-written as follows
C
V
= Q
G
∆P
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abdulbasit137@hotmail.com
control v/v depend to pv bcz pv i mean process variable
flow.flow types laminar,turbulense .transational, & flow
which gas flow, fluid flow,. another we done the cv size
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ganpat002
Cv=q/[[change in pressure/specific gravity]^0.5]
| Is This Answer Correct ? | 3 Yes | 9 No |
What is mean by Adapter block and net block?
can you tell me how many stages in steam turbine of 10 MW power plant
what is the diffrence between pressure safety valve & pressure relief valve....pls
in any transimitter (flow/level) there are three terminals for supply& test (+,-,+)in two wire,24VDC given to Tx.,but how 4-20 ma signal travels thru same wire (as it is for 24VDC input supply)?
What is the cascade control
How to convert 0-2500mmH2o into kg/hr? Or how to convert mmH2O into kg/hr,t/hr etc
WHAT IS THE DIFF BETWEEN FREQUENCY AND INTENSITY?HOW IT WORKS IN FLAME SCANNER ?
What is the difference between a PLC (Programmable logic controller) and DCS (distributed control system)?
flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...how to solve this problem when we apply 375 mmwc it shows 16 ma
i am going to attend ongc exam this coming june for Graduate Engineer Trainee post if anybody knows the question pattern or have experience plz share it with me
re i got gre score of 950,and toefl of 69 is this score sufficient actually my husband is presently in US i need to go please help me
What is offset in a control system.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)