Why do we need to install hook-up line differential pressure
type level transmitter when the differential pressure type
level transmitter with capillary are available?
Answers were Sorted based on User's Feedback
Capillary level transmitters are the best for just about any
application but they are very expensive compare to a normal
DP Cell with tubing.
The problem with these capillary transmitter installations
are that a lot of installations and designs are done without
flushing rings and equalization tubing and valves. This then
have to be installed afterwords since they are needed during
calibration once you start working on vessels with a process
pressure of 10bar and up. Without these the calibration will
become more inaccurate the higher your vessel process
pressure is. Be aware we still have static alignment
problems even in this day and age of smart technology.
Unless you do a process zero before your calibration you are
going to pick up problems and the only way to do a process
zero is if these flushing rings and tubing is installed from
the HP to the LP tap off points.
Good Luck
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kinst
I don't know the answer of the question. that's why i asked
this question.
| Is This Answer Correct ? | 0 Yes | 5 No |
in any transimitter (flow/level) there are three terminals for supply& test (+,-,+)in two wire,24VDC given to Tx.,but how 4-20 ma signal travels thru same wire (as it is for 24VDC input supply)?
How to Calibrate Ultrasonic flow Transmitter in Field
what is use of communication wire in multipare cable(oil and gas field), why this communication wire not used in single pair cable?
Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?
WHAT IS THE DIFFERENCE BETWEEN A TRANSMITTER & A SMART TRANSMITTER.
What is compensation for flow ? Why we use compensation ? What are the factors of different compensation ? We not use then what problems may happen ?
How to calibrate and check thermal mass flow meter of Make thermal instrument company inc model 60?
Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?
i have an interview in Qatar Petroleum. So please provide the all details abt fire & gas systems
What are use of positioner.
Explain the working of an enraf level gauge.
Define the terms Accuracy, precission, Spam, process tolerance while doing calibration of an instrument? Explaini with an example?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)