How can claculate to attain the desired PF in the line (
HOW Much KVAR is required ) Pls Give the formula?
Answers were Sorted based on User's Feedback
Answer / sivarao
From power triangle
KVAR=KVA*sin(theta) and cos@=KW/KVA.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / manjunadh
according to this formula we can easily find out the power factor PF=KW/KA.
using this formula we can easily find out the kva.
Is This Answer Correct ? | 0 Yes | 0 No |