How many earthings are provided for a 250KVA distribution
transformer?
Answers were Sorted based on User's Feedback
Answer / vilas
As per rules four earthings are required.
two for neutral. star point
Two for the transformer tank i.e.body of the transformer.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / ars326
1.Transformer tank
2.Neutral
3.lightning arrestor
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / deadzg_devil
Mainly two types of earthing are provided:
1)System Earthing:The neutral is connected to ground so that in case of imbalance the zero impedance current may pass thru the ground.
2)Equipment Earthing:This is provided to safeguard the outter body of transformer in case any fault occurs or any live wire touches the ground , it can redirect the current to ground.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ram
minimum 3 earthing. 1- neutral earthing, 2- body earthing &
3 - common neutral body
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ullas
mainly two earthing.
1. neutral earthing.
2. transformer body earthing
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / sumudu
Two earth banks for neautral; Common earth for Transformer
body & Lighting Arrestor.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.prakashchandra
Answer No. 1 is correct.For neutral, two distinct connections
Is This Answer Correct ? | 0 Yes | 1 No |
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
If the characteristic Impedance is equal to load Impedance then…… a) voltage will be increased b) power transmission is zero c) …… d) max. power is transmission to load
How to calcluate the current by means wires/cables in square mm
What are the types of transformers according to the arrangement of iron cores?
Why we make earth connection with Transformer Body and What will be the minimum size of copper wire as per code with respect to KVA rating of Transformer?
How many different speeds can be obtained in cascade control of two induction motors?
when we should use Central Battery system and UPS system and why? in other words, what are the differences between the two systems?
why dhyedration test required for transformer oil once in a year
Can any horizontally mounted motor be used as vertical?
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
what is EBXl (electron beam cross linked ) cable ?
What type of DC motor would you see for a lift?