Answer Posted / prasad

POWER FACTOR IS COSINE OF ANGLE BETWEEN VOLTAGE & CURRENT
IN AC CKT. HOWEVER IN SIMPLE TERMS IT CAN BE DESCRIBED AS
EFFICIENCY FACTOR OF LOAD IN p.u. IT SIGNIFIES WHAT AMOUNT
OF ELECTRICAL ENERGY IS REQD BY LOAD WITH A GIVEN P.F.
THUS IF TWO MOTORS OF SAY 80 KW WITH ONE HAVING P.F. 0.8
& OTHER HAVING PF 0.85, THEN FOR RATED LOAD FIRST MOTOR
WILL REQUIRE 100KVA WHILE OTHER MOTOR WILL REQUIRE 94.1KVA
OF ENERGY

Is This Answer Correct ?    6 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the difference between indoor and outdoor transformer

5350


3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??

1030


What is earth system using on the floater TN-S or TT. Iam not sure and what ICCP

1360


what is destructive and non-destructive testing of welding

1309


i need the curve duty cycle and amper for (150 kva @50% dyty cycle) transformer turn ratio :19 and vin 400

1734






how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

1515


What is the lower limit of break-down voltage of converter transformer.

1534


What is line resistance of cable & how it can be measured ?

1062


Can i replace Earth leakage relay to the faulty Earth Faulty Relay

1137


how to set relay setting? and example calculation...

1605


What is the purpose of using busbar mounting fuse?

1672


what is the stear deltaprinceple?

1488


How to check the Bushings of the transformer?

1363


Either It Possible a dc Motor to Run On Ac Drive [ Ex : ACS 800 , Yaskawa F7 ] If it is Possible How Pls Inform Me dinesh_elect_eng@yahoo.com

1649


State the points to be considered for selecting a particular type wiring.

1722