what are the advantages of Horizontal isolation breakers v/s
vertical isolation breakers in medium voltage switchgear class.
Answer Posted / hemantha madurapperuma
The question should be re-phrased. Though there are numerous advantages of the vertically isolated MV switchgears, the design has been phased-out altogether.
The main advantage of the vertical isolated design, all critical insulation surfaces being vertically disposed , least pone to surface contamination.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What is the type of feedback used in an op- amp schmitt trigger?
What are the main parts of central chiller plant? Explain the function of each stage.
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11
How to select the cable and voltage drop in circuit?
WITCH CARDS IN USE IN FIRE CONTROL PANEL.
If I want to connect a capacitor bank on the HT side of a 11kV/415V, 3 phase delta-star distribution transformer to supply Reactive power to it..what practical specifications of a Capacitor bank that can i've??please reply..
critically criticize the application of ring main unit in power system
PIU how does work?
how can we select the type of wire.what factors we have to look on it , do we have some formula to calculate it. please guide me on it
What is the difference between hot and cold loop testing?
Why the efficiency of generator is more than motor in swinburne's test
howmany electrician should maintain for a 1000 kva used plant... in kerala..
Can you please explain creepage distance in detail, for a 6.6kV cable head what must the distance be and how do you determine it?
Meaning of ingrace protection for motor.for ex IPXY
in science exhibition how lamp can blink when you clap near the lamp ? thank you