Answer Posted / raybuilders
kVA*pf*1000/746=HP
1hp=746watts
Pf means power factor, it simply mean how efficiently the device uses electricity.for motors-the industry standard is 60% while for other devices it is 80%.
Assuming it's not a motor and the kVA is 1
kVA*pf*1000=1*0.8*1000/746=1.1hp
If is a motor, hence.
1*0.6*1000/746=0.8hp
Regards.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
Is it possible to download the Siemens Selection Chart(TYPE 2 coordination) for 1) fuseless selection 2)Fuse selection
What is mean 2XWY
WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?
Define damping ratio.
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
In synchronous motor, how the field current is related to armature current..i know its inversely proportional..but concept wise...i was nt clear....pls help me...
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
What are stable systems?
Can we Co-ordinate relay in Load Break switch?
redundant connection in contactor?
I Need standard operation procedure(SOP)for 500kva Oil type transformer oil filtration & Procedure for IR value checking.
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
What is Primary And Secondary Injection Test of Relay and Other Electrical Devices. How IT is carried out.
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?