How many battery required for an 3kva online ups with 3 hrs back up with usage of 3 fans,3tube lights

Answer Posted / shri...

Connected load = 3 Fan (70 watt each approx) + 3 Tube lights (40 Watt each approx)
Load = 330 Watt
Battery back up time 3 Hrs

Required minimum 12V 1 no 120 AH battery

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts

1660


what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker

4555


what is the meaning of osr in transformer.

1549


is the value of inductance depends upon the value of thitha in doubly excited machine??

1571


what are the installation procedure of high voltage power transformer,CT,CB&PT?

1617






What is Primary And Secondary Injection Test of Relay and Other Electrical Devices. How IT is carried out.

3024


what is tri state logic gate

1622


Explain dc generator with its types?

642


Differentiate between voltage and current feedback in amplifiers?

633


What is the differentional relay...what is the work of this in power Tx. how it is works..

1453


How can we calculate the KVA rating of a Distribution transformer from its core details?

1608


what is interpose? where it is used and why it is used?

637


Which power will flow first if we switch on a motor Active or Reactive? How?

4384


In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?

1610


What happen when neutral point connected to core balance current transformer? (Neutral point of an alternator of a 180KVA DG. Neutral point connected to CBCT means enter to the CBCT)

1849