Do you know how to measure the earth resistance? if so
explain it
Answer Posted / meshach
Earth resistance, is measured by Earth Resistance Device.
Which a good Earthing Resistance is suppose to give:
1) E to N = 0.7 V
2) P to N = 228.6 V
3) P to E = 228.7 V
And Bad Earthing is:
1) E to N = 0.5 V
2) P to E = 16.2 V
3) P to N = 228.6 V
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
what percent do you derate your copper wire when you change from copper buss to copper wire
redundant connection in contactor?
why steady state stability limit is greater than transient stability limit ? How it can be explained ?
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
I am EEE student i want to improve my core side skills.how cn i approach it?
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
what is Different between Bilinear and Unilenier?
Why does amplifier gain reduce?
Why is voltage is required to be within permissible range for an electrical equipment?
how to calculate single phase motor efficiency ?
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
What is the difference between acs 550 & acs 850
what is the difference between earthing and unearth
how we calculate electrical load on a building according to area?