Can be ammeter and voltmeter used without CT? if not, what is the reason for that?

Answer Posted / sameer

if you are measuring current at the high voltage line have current 60Amp then you cannot connect the ammter directly you have required CT whose scondary is connected with the ammeter . same as for voltmeter if range beyound 750volt measure you need to connect voltmmeter to Pt

Is This Answer Correct ?    9 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the difference between electrical and electronic choke?

1479


why and how current drawn by battery charger depends upon the altitude where it is located?

1577


Why should we hire you over the others waiting to be interview?

2370


SIR, GIVE ME OPGW SAG CALCULATION FORMULA I AM DAE ELECTRICAL. THANKS

5985


What is the basis for framing the rules of block diagram reduction technique?

977






what is allowable ac mixing in dc

1547


If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.

1500


Name one of major transformer company in KSA ?

755


Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing

1471


In a large office how do we calculate required number of light fittings, assuming fittings are 4x18W or 2x36W fluorescent fitting ?

1427


Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?

1065


What is excitation in case of dc motor?

685


where was current transformer protection units used and why??

1549


What is servo motor? what is its purpose?

1601


What is the differance between 2 dc motors of armature voltage 660 v and 440 v?

1555