Double Busbar Scheme for outdoor switch yard system (132kv) step up power plant
Hi friends
1. in this system both busbars energized all the time.
2. what is the meaning of main BB and transfer BB,
3. step up transformer connect main bus bar all the time or both BB connected through DS switch .
4.bus sectionalization means ?
thank you.
Answer Posted / k.prakashchandra
When one line is connected to a BB ,the other is the transfer BB . You can energize both BB either independently or using bus coupler . Sectionalzation means splitting the bus bar into sections lengthwise
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what are factors to be consider in electrical installation like load factor,diversity factor .....
what is automatic voltage regulator?we can control the vlotage by using fuzzy controller in matlab?why we go for fuzzy?
why ups rating in kva? and why ups are in parellel?.why isolation transformer is used in ups?
What are the disadvantages of hydropower?
How can we calculate the efficiency of a Running (On-Load) Motor ? What parameters are required and what is the method ?
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
can we synchronize star system generators with delta system generators?
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
Where I can get the sample question for post of Junior engineer electrical-II For RRB Bhubaneswar.
what is the vvvf in the dumbwaiter?? or lift. what is the actual process?/
Define maximum demand?
What are the factor to be consider for CT selection in 132kV substation?
What is Control & Relay Panel? And Remote Control Center?
Why do we need a separate control desk & PLC control panel in Boiler plant or coal handling plant? Can we provide cost effective Control desk cum PLC panel. Is there is an specific need for control desk.. kindly advice.