what is the bus bar size of 2700 amp ACB breaker ? and what is
the cable size ?pls detailed answer ?
Answer Posted / koti
Bus bar = 2 nos of 200 X 12 mm Al
Cable = 5 R X 3.5 C x 630 Sq.mm Al
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
what is the easiest method of short circuit current calculation ? pls. derive with a mathematical example in real life application.
how make megger test for control cable like 12c x 1.5mm and what it apply voltage and test timing details.
Define active filter?
we have 3 single phase transformers. how will we generate 6 supply from 3 phase supply input
why US countries maintains 110v and 60HZ
What are the disadvantages of thermal power plant?
What is the maximum and minimum rating of UPS?
What is meant by celling voltage & current in excitor ?
what is plunger and what's the use of it in motor alignment?
the problem faced on star or delta winding connection??
Is it required to do earthing in 2nd shop if earthed armoured cable is laid from 1st shop ?
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
what is the condition for YnD11
After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.
What is slip in an induction motor?