what is the bus bar size of 2700 amp ACB breaker ? and what is
the cable size ?pls detailed answer ?
Answer Posted / koti
Bus bar = 2 nos of 200 X 12 mm Al
Cable = 5 R X 3.5 C x 630 Sq.mm Al
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
Define the overload capacity of the motor?
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
What is deference between MCB & MCCB & ISOLATOR
What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?
magnetizer priciple
Air circuit breaker safety
what curve and rateing would you use for a three phase 0.75kw motor?
how to select correct size of power cable for inverter duty motor
In convertor can we use rectifier thyristor in place of invertor thyristor with explain.
How servo stabilizer works.
What do you mean by an instrument transformer?
to vary valtage from 0 - max a variac is necessary . so how to design for high power applications nearly about 200KW power
What are the relays in ACB and VCB
what is the mechanism of operation of brushless dc motor why is it more wexpensive then ordinary permanent magnet motors
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?