Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

In a 3 phase system a neutral exists so that any unbalanced
currents can flow through it towards earth.... but a phase
demands a particular current as per the load attached to
it....then where does the extra current come from the goes
in the neutral??....I mean in an unbalanced system a phase
demands a current as per its load attached....then where
does the unbalanced current come from??

Answer Posted / kj

In a 3 phase system the usual way of connecting the
transformer is in star to have a neutral. The current
flowing in the neutral does not flow to earth but to the
star point. The star point is the opposite end of the
windings where the phase is connected and the 3 are joined
together. The current in a balanced 3 phase system for
example a 3 phase motor flows through the phase wires and
not the neutral. An unbalance would be where something is
connected to a single phase and the neutral. This would be
lights for example. Here the current flows from the phase
and back through the neutral.

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What are the protections for safe running of electric generator?

2250


Why reactive power is needed in a power system? How is it being absorbed or delivered by alternators? For reactive power control we are changing excitation but reactive power absorbing or delivering related to stator. How these two are interlinked? i want a detailed explanation with necessary expressions and figures?

1896


What is meant by system?

1057


5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch

3806


If not into production, how far did you follow the design and why did not you see it into production?

2166


Phase control and integral control are used for?

2319


Write the programming software name for LG, SIEMENS,Messung,AB

2027


what is the effect of vector group while phase sequence of a generator changes,whether the vector group changes or not

2094


how the B-H loop obtain under the static condition

2317


What is the most accurate way of testing ELCB?ELCB is better than RCD?

3325


what is the basic construction diffrance between servo motor ans sqiralcage induction motor

2460


What is Antipumping Function & If we have C.T how we find the Ratio ?

2022


What is the theoretical reason for the size of a zig zag grounding transformer to be 1.732 times less than that of a wye-delta grounding transformer used for the same application?

2267


how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???

2018


What are the limitations of Kirchoff's laws?

1580