what is intrument termination
what is commisioning

Answer Posted / james c

When installing instrumentation, cable is run from the marshelling cabinet, or some control system to the instrument in the field. The act of attaching the cables to the actual electrical terminals of the instrument or input output terminal at the Transmitting or receiving end is called Terminating the instrument. I.E instrument termination. Usually the instrument loop is installed in stages, where the instrument is physically mounted in the field, cable is pulled and run in cable trays or buried in trenches, and the ends of the cables are terminated.

Once prior to completely terminating a loop, the cable run is normally loop tested. I.e. Point to Point continuity checked. Once the cable is found to be good, and the instrument terminated, calibrated and tested to be functioning at the control system, the instrument is said to be commissioned. I.e ready for service. That is called commissioning. Usually commissioning forms a entire stage/phase of its own in a project.

Is This Answer Correct ?    8 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

please any body have most important data for study for saudi aramco test of instrument QC thanks email shahnaveedullah@gmail.com

1249


How would you choose differential range?

722


what is the difference between -24 : +24 & 0:24 and where it use?

1641


sir i m preparing for BARC but i am not getting any papers to prepare for this exam so please send me some sample papers to my i.d for the preparation of barc.

2012


how do calibrate the valves.. with clear manual

1565






how to tune siemens sipart electro pneumatic positioner..plz tel me..

1669


Hi i m B.E. In elect. & comm. I m workin in bio mass plant from 6 mnths as inst. Engg. but now i m in dept. Of operation as shift engg...which is best operation or inst. 4 me? M confusd..plz help and reply me..

3308


where i can get training in INTOOLS and PDMS in Delhi-NCR OR north part of India. please reply with ur ans. at arunsamkaria@ymail.com

3083


Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.

1650


when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??

1723


In apron feeder how TPH is calculated?

1193


What is the principle of capacitance type level transmitter?

678


in valve is constructed as per SME B 16.34, then which standard is used for fire testing of valve?.

1586


Why do you want to work here

1831


what is span value and zero ? and how set ?

1075