what are different type of triping equipmen like MCB,MCCB
and their differences
Answer Posted / mukesh sharma
Tripping devices are circuit breaker,mcb,mccb,rccb,elcb
MCB: Miniature circuit breaker
MCCB: Molded case circuit breaker
RCCB: Residule current circuit breaker
ELCB: Earth leakage circuit breaker.
mcb can be used up to certain level of current it can also
used as a switch but it can Connect only on single conductor
or wire for two or more wires we can use different circuits
manufactured by multiple mcb like Dp,Tp Tpn.
mccb it can be used at three wires for large ammount of
current flowing (above mcb rating) usually above 100A current.
mccb & elcb both are used for human protection but tripping
method of both is different elcb will trip by sensing
cuntunity between phase and earth when ever mccv will trip
if there is a difference in current flowing between phase &
neutral more than or equal to 30mA basically mccb is advance
version of elcb & it is letence.
in my openian mccb is more better than mccb.
| Is This Answer Correct ? | 1 Yes | 3 No |
Post New Answer View All Answers
Why should we hire you over the others waiting to be interview?
What is acsr cable and where we use it?
i have a 1500kVA transformer what is the kWH meter i need to use?
what is inter connected dc generator?
Why control of DC motor is simpler?
Hello Friends, How can we recognize the CT Star Point is S1 or S2 in case of Electro Mechanical Relays and what is meant by Restraining coil in relays and what is the purpose of that.. thank you in advance..
The electrical energy required to raise the tempreture of a given amount water is 200 kwh. If the heat losses are 20%, the energy required is?
HOW TO CALCULATE EARTHING SIZING?
What is gross error?
How will be the single line diagram of series trip HT breaker? how it works?
Is it possible to implement Restricted Earth Fault protection for a transformer without neutral CT?
how to calculate IR value of 33KV cable ??
how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you
what is the difference between transformer,converter and transducer
How to work E.L.C.B and how to connect in circuit.