can you give main difference between ELCB And RCCB?
Answer Posted / muhammed siraj khan
RCCB:residual current circuit breaker (RCCB)
It measures the difference in current between live
and neutral conductors of a system.In normal conditions it
is equal,If not than it indicates that some faulty current
is flowing other than live and neutral and result in
tripping the device/circuit
simple.
ELCB:
Detects faulty currents passing from live to the earth wire.
ELCB Will not work properly if the earthing is impropoer
Note: For tripping the ELCB,all equipment body should be
earthed.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
Write the current equation in series RLC circuits.
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
why can we use cosine wave instead of sine in ac supply as both have same rms vale and ripple factor
.php|
determine two methods to find loose connection in operational electrical system?
Salient pole alternator is more stable, why?
please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5
What was the Dg set radiator and lube oil temperatures trip in ACB
What is the loss of transformer of 220kv/11kv, 63/80 MVA and 18.05% impedance
what is the use of power transformer in GSS.
How to calculate multiplying factor of dc energy meter
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
why are u join ntpc
The loads are connected with phase and ground then why current flow as the loads ?