If an Instrument has 550 ohm internal resistance and the
cable used for that instrument is 0.5 ohm per meter
resistance. If the voltage is 12volt.How much length cable
can be used? Please tell me its Calculation formula.
Answer Posted / c heman
Assume it is a 4-20 ma tx. 20ma*550= 11volts. minimum
supply is required. so allowable voltage drop is only 1
volt.
so max. 100meter u can use.
got the answer, don,t foget to say thanks.
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
what is the process to make control schematic ?
How is flow measured in square root?
Explain plc level and its type?
How to Calibrate Ultrasonic Level Transmitter in field
whatis range of marcury filled tempereture gague
KAlman filter code for two dimension?
What is 1:1 redundancy ?
Basically iam Instruemntation Engineer, but Iam interested in Instruments design engineering, so plz guide, is there any course, training or Softwres to become Instrument design engineer??.
what is the current pay package for an instrumentation engineer having 2 years of experience in cryogenic technology???????
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
Describe how to use megger to measure the earth resistance and insulation resistance
how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?
how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)
what is the vital subject for scoring bhel exam&what is the question pattern
what is the input to be given in digital flow meter during the the calibration time?