how to calculate capacitor rating for an induction transformer
ex.for 12 mva furnace calculate capacitor rating
Answer Posted / krishna.bagavan
for 12mva at 0.8 pf mw= 0.8 x 12 mva
= 9.6
as per p.f.triangle mvar=square root of mw2+mva2
ie. square root of 9.6 x 9.6 + 12 x 12.
= square root of 92.16 + 144
=square root of 236.16
=16 mvar
Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
what is the difference between delta delta and star delta connection transformer? why we use delta delta transformer since it need earthing transformer for grounding?
What is resistance reading of earth copper rod with grid and without grid?
plz tell me,ht and lt panel terminals in substations explain beiefly
what is the formula for computing cable tray size & capacity
Explain what is electric traction?
How do we calculate over and under frequency tolerance from generator data?
What is advantages of VSCF wind electrical system?
WHAT IS MEANT BY SHEATH VOLTAGE IN 132Kv cable?
What if the difference beween internal and exrteranal LBB?
Any Electrical Engineering jobs?Please refer for interviews. Thank you
How to setting the volume of RTCC panel AVR (11kv) controller
What is the high series capacitance winding on high voltage power transformer ?
Why saturation region slowly shifted in the left side?
what are the Alarm, Trip & Safety equipment (Issues) present in Power Transformers pls Mail it to ashokbabunhce@gmail.com
Please provided formula for calculate the cable size from step up transformer to M.V panel, run overhead aluminum cables, total load is 5mega watt, total length 900 feet.