power 148kw i need exat cable size in 148 kw in 3phase what
size of cable can i used.
Answer Posted / mahendran
1 kw = 2 amps ie 148*2=296 amps
240 sq mm will carry 220 amps you make 2 * 240 =480 amps
this is actual amps for safety we give 755 load to the cable so
240*75%=380amps
150sqmmwilltake 180amps ie 2*180=360amps75%load
360*75%=270amps its less then your load
so you can select 2*240 sqmm cables
| Is This Answer Correct ? | 0 Yes | 5 No |
Post New Answer View All Answers
Where can I get CPWD electrical specifications & Shedule of rates? Please help me
why on axial hitting up of air blast on hydrogen produced in oil circuit breaker,temperature rises of the core of the arc?
how generator load test is conducted?what are the steps?
State the types of distortions in amplifier?
How to select a contactor? How many types of contactors are available
Is there any specialised book to refer about fault level calculation both in MV and LV side??
What are the applications of different multistage amplifiers?Plz also write advantages of these amplifiers? Thaaaaaaaaanx
how balanced in star delta connection ?
Define ampere
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
What is a parabolic signal?
How does an induction motor start?
- two pumps must work with them at the same time but if the first pump start the second pump must delayed for some time to start also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it
If short circuit ratio is high is it bad or good for a machine then tell the reason...
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?