Why does the DC voltage needed is less than AC needed to
produce corona?
Answer Posted / akki
AC voltages are associated with skin effect and thus,
current flows effectively very close to the surface of the
cables. Therefore, resistance offered increases.
Since AC resistance is greater than DC resistance and corona
discharge is favorable in higher conductivity, therefore the
dc voltage to achieve corona is lower than the ac voltage
needed to produce corona
| Is This Answer Correct ? | 2 Yes | 4 No |
Post New Answer View All Answers
How to calculate VA rating for CT or PT or Control Transformer?
Is it required to do earthing in 2nd shop if earthed armoured cable is laid from 1st shop ?
Why is remote backup preferred to local backup?
what is control supply rating of a machine
with 3 phase board on a 63 amp rcd is it ok to have 6 electrical showers 2 on each phase and what problems could happen
what should be the acceptrd value of winding resistance for 2.5MVA transformer
Is it advantages of having star-delta vfd than normal star vfd , if yes why?
What if the difference beween internal and exrteranal LBB?
what is mean by NPS (Negative phase sequence)fault? what is the difference between EFR & OCR faults?
HELLO EVERYONE, I RECENTLY HAVE FOUND ONE PROBLEM, I WAS TAKING NO LOAD TRIAL OF AN HT MOTOR 920 MOTOR , 1440 RPM , 6.6 KV, WITH AUTO TRANSFORMER. AT 450 V, LOAD WAS 40 AMP AND SPEED WAS 250 RPM. BUT AS WE INCREASE VOLTAGE FROM 450 TO 480V, LOAD BECOME 41 AND SPEED REDUCED TO SOME RPM . SO WHICH PHENOMENON ACTED HERE FOR REDUCING SPEED.?? AND IS IT HAPPENING ALWAYS OR IT IS RARE? I ALSO HAVE FACED SUCH PROBLEM WITH FEW LT MOTOR ALSO.
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating
How many points does a Circuit can have?
what is the difference between electrical choke and electronic choke?
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
Why hydropower is called renewable source of energy?