What is the difference between Relay and Contactor
Answer Posted / m.senthil
Which is directly connected with the load is called contactor. whereas if the above same contactor is control the other one contactor, which is connected with the load, here the controlling contactor is called relay.
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
What is different bewteen low or high impedance busbar protection scheme
DC transmission
why we use the 100% and 95% stator earth fault protection for the synchronus generator ?
what will be the maximum winding temperature of 6.6kv HT motor 450kw, Full load current 49A. 50Hz Frequency.
hi guys please tell me the procedure for mesuring the coil resistance of 3ph induction motor?
Define newton's law of viscosity.
What will be in Mahagenco Trade Test Exam? I want to know the same.
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.
What is the power factor of an alternator at no load?
why we setting 95 deg and 105 deg in wti and oti of distibution transformer ? give the reson for that ?
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
How is the resonant peak, resonant frequency, and bandwidth determined from nichols chart?
If Dg set load increase 25%, How much increase fuel Consumption (15 kva 2 cylinder DG set)
why does the magnetic balance tests at transformer?