draw a circuit diagram connecting transformer OLTC- RTCC-
VCB-Marshalling Box otherwise Explain in words
Answer Posted / alleysyed
OLTC stands for On Load Tap Changer, which means that a user
can change the taps of transformer winding without
disconnecting the transfomrer from the supply. Taps are
changed in order to regulate the voltage. OLTC has number of
taps . They may be 10, 11, 16 , 20 or the customer specified
rating.
Marshalling box is a box in which manufacturer of
transformer bring alarm and trip contacts signalling from
the accessories associated with the transformer. For
example, Oil temperature indicator installed on the T/F
provide a signal of alarm when the temperature of oil
exceeds the specified limit of Indicator. If temperature
exceeds more, it send the trip signal to Marshalling box,
which disconnects the transformer from main supply and
vacuum Circuit Breaker is tripped. VCB is installed on the
High Voltage side of the TF in the HV Protection panel.
| Is This Answer Correct ? | 31 Yes | 5 No |
Post New Answer View All Answers
What is Meter MF if External CT Ratio is 150/1 , PT Ratio is 132/110 Meter CT Ratio is 200/1 & Meter PT Ratio is 110/1
5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch
Basic motor transformer generator
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
magnetizer priciple
Will an earth leakage trip be activated if the component or wiring is faulty on low voltage equipment.Example An electrical Cat Scarer placed in the garden and water gets into the wiring.
How many kinds of E.L.C.B and how to work E.L.C.B
what topics we have to concentrate for power grid et.written test.and tell what to read for english synonyms and antonyms.
What is power in wattage of 8.5 TR AC
what is the calculation method to design core and winding of a 200kva 3phase distribution transformer?
Why power genaration in India is at 50HZ while America its 60HZ
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?
what is subtransient , transient and steady stateac components
what is the value of combined earthing in general electrical circiut?