If a 3 phase transformer is a 500 kva using the formulae
500kva= 500000/433 x 1.732 = 666.71amps does this mean that
each phase on the secondary side is 666.71
Answer Posted / k.prakashchandra
The VA per phase is (500/3 KVA) 166.67 x 1000 , phase
voltage is(433/1.732) 250 V.Then current in each phase is
166670/250= 666.68 A
Is This Answer Correct ? | 8 Yes | 4 No |
Post New Answer View All Answers
What is EMC filter in VVVF Drive ?
hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.
Draw a 230kv two-bus bar system showing the following. 1.Two generators (150MW) each connected through one 15.75/230KV transformers 2. 1 outgoing lines 3. Two 230/130 KV transformers 4. BUS PT's 5. CT
Basic motor transformer generator
Define bibo stability.
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
Explain bypass capacitor?
Will an earth leakage trip be activated if the component or wiring is faulty on low voltage equipment.Example An electrical Cat Scarer placed in the garden and water gets into the wiring.
how to find out cable size if load is 2800 watts, 230 volts AC supply and load distance is 1800 meters
What is meant by stator? What is meant by rotor?
How to calculate multiplying factor of dc energy meter
what is difference between bus coupler and auto transfer switch
How halogen & merquery lamp works.
I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL. 1-IS BETTER WE USE CABLE? 2-IS BETTER WE USE BUS DUCT? my transformer rate power is 2500KVA
Why we are going for converter transformers for DC drives application instead of distribution transformer?