Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is meaning of sympathetic tripping with respect to
relays and give the values for current carrying capacities
for copper and aluminium cables from 16sq mm to 500sq mm

Answer Posted / jaimini soni

Sympathetic trips are undesirable relay operations for
unbalanced- or high-load conditions which
occur during or immediately following out-of-section
faults. The root cause of the sympathetic
trip problem is the type and connection of loads served by
distribution feeders. There are two
classifications of sympathetic trips: those which occur due
to delayed voltage recovery
conditions, and those which occur due to the load unbalance
during an out-of-section fault.

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Dear friends I want to design busbar for1600 kva transformer(i.e2100 amps) what are all the factors to be considered before selectinga busbar what are all the standard sizes of busbars what is the formula for finding current of copper and aluminium busbar

1902


what ispositive, negative, zero sequence impedence?

2030


define hysteresis loss, eddy current loss and windage loss

1998


what are the preventive maintanance actions taken for air circuit breaker? please answer me

2035


Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.

2380


what is the principle of operation of CFL ??

2670


I want formula to calculate current loss with distance in km.I searched many sites but didn't right answer.Plz reply me

2077


sir, iam a electrical engg graduate and i want to go in automation sector and for this i have decided to do industrial training for this,plz suggest me some good institute for the same in delhi,ncr. my degree percentage is 58%, can i get job after doing training, plz help....

2039


Why increase in current leads to increase in conductor temperature?

1141


Explain about retrofitting of machine tool.

1900


What is the power requirement of tamil nadu for one month?

2021


HOW TO CALLICULATE RESITENCE,REACTANCE AND IMPEDENCE VOLTGE OF TRANSFORMER 13.33 KVA 144/240 VOLTS 93/56 A WITH FORMULA

1978


what is the interrelation between voltage current torgue speed and magnetic flux in case of different types of electric motors

2104


we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?

1922


Sir pl provide 5 year sample paper for post junior engineer(electrical).I have currently applied for junior engineer (electrical) on RRB Ajmer

3634