What current can be carried by 25 sqmm copper cable safely?
Answer Posted / k.prakashchandra
Both the answers are correct except for calculation error in
No. 1.You have to consider IR drop also. Upto 25 m length 4
A/ sq mm and upto 100 m 2.5 A/ sq mm may be taken as
carrying capacities.
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
what is meant by flywheel and its role in retardation test
What is a slack bus?
how to find three phase complex power in per unit and MVA?
How many types of circuit loads are there in a common electrical circuit?
DG SET BLOCK DIGRAM
as a electrical student why should i hire you?
Incoming line 11kv And transformer capacity is 2500kva. Consumption load is 1300A. Then fuse capacity is 11kv line.
What are the basic & Majour problems in UPS ?
what is circuit recombiner and how it is different from circuit breaker
how to define tell me about self
What is grid collapse? what is the reason for it?
Why does the radius of armature is less than the radius of pole shoe?
Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.
What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?
Describe Non I.S. Earth System and why is it used?