we are small scale industry in production of rice & rice
bran. Pls let me know how to take contract demand for our
industry.. (for information we have total 600.hp)
Answer Posted / k.prakashchandra
Contract demand is based on demand factor which to be
assessed or obtained from a similar industry.Once you enter
into agreement with the supplier ,you will have to pay the
demand charges during the entire period of agreement.If you
take the demand factor as 0.8 ,your CD will be 425 KVA at
0.85 pf..You can start with a lower value and ask for
sanction of additional CD if the MD exceeds the CD.Normally
you are unlikely to be penalized for exceeding CD during one
month ,depending on prevailing supply rules .
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What is core CT & it's function?
What is meant by reset level of the relay?
An ELHNC 80amp 240v 30mA RCD is tripping periodically, every 30 - 180 seconds is it safe to disconnect the protection circuit?
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?
What will happen if we on 200kvr capacitor bank(11kv in bus)If there is low load on transformer (1.5 mva 33/11 kv)
how to increase senstivity of ct
Is Transol transformer oil comparable to nynas nytro libra?
what is meaning of bus riser
Hoe do calculate the Cable size for Amps rating ?
wow to calculate the transformer rating(KVA)
how to set the time in digital timer ?
in 1-phase 230v,how in 3-phase 440v. in each phase in between 230v.
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
how to calculate IR value of 33KV cable ??
WHY THE DIMENSION OF TWO SAME RATED MACHINE IS DIFFERENT ?