Answer Posted / priyesh gajjar
pt100 is a type of resistance temperature detector ( R.T.D.
).it is use for temp. measurement.resistsnce is linearly
vary with tempature. it has 100 ohm resistsnce at odegree
celcius.
| Is This Answer Correct ? | 9 Yes | 2 No |
Post New Answer View All Answers
How good are you in resolving the commercial issues to Employer's advantage?
how to calculate
what is method for testing CT
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
Why is the starting current high in dc motor?
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?
EXPLAIN USE OF ROCKING ARRANGEMENT IN ELECTRIC HEATING?
What is the tension required for the 25000 CFM AHU belt
what is the common earth
State any two nuclear power stations in India, with their generating capacity.
why on axial hitting up of air blast on hydrogen produced in oil circuit breaker,temperature rises of the core of the arc?
What do you mean by per capita requirement of electrical energy in india
Percentage losses in power generation?
is ac supply can store
WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB