Three way plug point is there ,in that plug why we need
earth pin is bigger than compare with phase and nutral pins?
Answer Posted / dhivyabharathi
The earth pin has to send fault current to earth.so, the
resistance of that path should be low.to get low resitance,
cross sectional area should be more. it can be understood
from R=pl/A.so the cross sectional area of tat pin should be
high.
Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
what is the difference between active power and reactive power and apparant power in practical as well as theoritical
What is dc current source? Differentiate between ideal and non ideal current sources?
Why AC & DC capacitor are use in UPS ??????????????????
what is fault level of power system ?
why is using sensor?what is differece between photoelectric and proxmitty?
What is the function of electron gun assembly used in crt?
WHY THE RATINGS OF THE TRANSFORMER IS 33KV WHY NOT OTHER???
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
What is open delta Xformer? It's adavntages & Use?
Draw torque - speed curve and load curve of induction motor? mark operating point ?
why the projects getting loss?
If a surge divertor is required to be protected by 32 amp C Curve Circuit breaker does this limit the amount of protection from surges that you will acheive
what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.
On what basis do you decide the ONAN (Oil Natural air natural) or Dry type transformer for a project?
WHAT IS THE TOTAL POWER GENERATION IN CHHATTISGARH?