WHAT IS OLTC OF TRANSFORMER? WHERE IS ITS USED EITHER ON
PRIMARY OR SECONDARY SIDE OF TRANSFORMER?
Answer Posted / mayank
OLTC means...ON LOAD TAP CHANGER. It is provided on the HV
side of the transformer. On HV side as the current is less
we can easily( not that easily..) switch over to different
voltage levels thus producing minimum chances of arc
production. While on the LV side as the current is very
large On load tap changing almost becomes impossible.
| Is This Answer Correct ? | 15 Yes | 2 No |
Post New Answer View All Answers
calculate external resistance values to add to the rotor of a slip ring induction motor. STATOR- 415 V, 3 phase delta, 1100 A, 50 Hz, 1490 rpm, pf 0,86 ROTOR - 660 V, 590 A, 50 Hz. STATOR current at each steps STEP1-600A,STEP2- 800A,STEP3-1000A,STEP4-1100A.
What facility we get after CT secondary earthing and how?
what maximum range of star & delta in hp or kw ?
what is meant by flywheel and its role in retardation test
can we use trip light with bus coupler?
How to measure the earth resistance value in a concrete pavement(flood light area)?
give me applications of sequence bridges . (used in 3 phase un balanced systems)
in a silicon diode we can measure .7v in a voltmeter.but why we can't use this voltage for using?
Where is the best place to mount distribution panel in a house.
why dimmerstate always connected in star connection? what will happen if it connected in delta?
what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?
HOW TO CHECK THE VECTOR GROUP OF A TRANSFORMER YD11?
I am inpecting a 10kVA UPS what tests should i do and should i observe?
What is distance between electrical panel to land ?
Air refrigeration cycle works on the