if we convert watt into kva,which one formula use by us,pls
tell me?
Answer Posted / sheikmohammedilyas
IN three phase motor,
Power= square root 3 *v* i* cos teta
-------------------------------
1000
1.732 *V*I*cos teta
W = -------------------------------
1000
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
HOW TO DESIGN THE body EARTH cable(Copper Conductor) size for 60KVA UPS?
What happen when neutral point connected to core balance current transformer? (Neutral point of an alternator of a 180KVA DG. Neutral point connected to CBCT means enter to the CBCT)
What are the factor to be consider for CT selection in 132kV substation?
do anyone out there know where to find a compleete list on acronyms/abbreviations used in offshore electric engineering. MCB - Micro Circuit Breaker, MCCB-Mouldes Case Circuit Breaker, ELCB-Earth Lekage Circuit Breaker, ELMCB- etc.....
why we used dc supply for field in dg set
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
what is counter poise conductors
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
H.t motor 6600 volt to same motor lt supply 440volt supply applyed to h.t motor to effect....
What is a signal flow graph?
Define stepper motor. What is the use of stepper motor?
Difference between HRG and NGR. Are they both the same thing
what is the major difference between LIBBP & HIBBP.. which one is most preferable..
What are the three types of compensators?
PLEASE INFORM ABOUT THE IDEAL TEST RESULTS OF MAGNETIC BALANCE TEST OF TRANSFORMER 33/11 kv DELTA-STAR T/F