IN WHICH MODE THE TRANSFORMER WILL GET A MAXIMUM OUT PUT
VOLTAGE. ASKED FOR POWER GRID EXAMINATION
STAT-STAR,STAR-DELTA,DELTA-STAR,DELTA-DELTA
Answer Posted / manish
Delta-Star
In Delta Primary Winding the Line Voltage is same as the
Phase Voltage (Let V volts), the transformation ratio is
same for all configuration (Let V'/V) & in Star Secondary
Winding the Line Voltage is SQRT(3) times of Phase Voltage.
Thus if Input Voltage is V
Then Delta Primary Phase Voltage = V volts
After Transformation Star Secondary Phase Voltage = V'
Thus Star Line Voltage = v' x SQRT(3)
Is This Answer Correct ? | 4 Yes | 1 No |
Post New Answer View All Answers
What is the gross weight to copper ratio in slip ring induction motor of 4000 HP,6.6 kv, 372amp, 992 rpm GE motor.
What is the practical way to calculate the cable size for known ampere load?
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"
Fantio of tranformer
what is booster? and how it is connected in a circuit?
Show the schematic arrangement of diesel power station layout and give its principle of operation.
explain the mode of metal iranafer in Co,welding
What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?
what are the basic insulation levels & what its Unit
TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2
explain all the classes with example
What are m circles?
what's producer of XLPE cable laying in undergroung
If the line voltage is reduced to 75% of its rated value then by what percentage current will reduce ?? 75% 25% 50% no change and why ?
what is working process of star delta controlling circuit ?